Controller Power Fault (Mercury)
The Controller Power Fault (Mercury) trouble condition indicates one of the following for an ADC-AC-LP1502 controller:
- The ADC-AC-LP1502 system has reported a loss of AC power
- The backup batteries to an ADC-AC-LP1502 system are not properly installed
- The backup batteries to an ADC-AC-LP1502 system have been depleted or are non-operational
How to resolve
If using the ADC-AC-LP1502-PSE:
The power fault input terminals come pre-wired in the ADC-AC-LP1502-PSE kits, therefore you are only required to install a backup battery power bank of 24V DC to the FPV4 main power supply board.
Backup batteries need to be connected to the FPV4 within the ADC-AC-LP1502-PSE kit in the following configuration:

Note: If backup batteries are not attached or are depleted, this trouble condition will be present.
If using a third-party power supply with the ADC-AC-LP1502 system:
The AC power fault reporting terminals on the third-party supply must be a Normally Closed (NC) circuit. If the AC power fault terminals are Normally Closed (NC), connect them to the FLT and GND terminals on the controller. Refer to the third-party power supply's manual for AC Fault condition causes and backup battery installation instructions.