 Training Required.pngHave you taken the Smarter Access Control training course yet? 

 

Note: This article specifically covers the installation of the X1100 Door Controller (ADC-AC-X1100). For instructions on how to set up a broader access system, see HID Aero Series Smarter Access Control - Quick Start Guide.

This course is recommended for every installer and is required for three reps per Service Provider before Access Control hardware can be added to an Alarm.com account. The course should be completed at least 48 hours before the first customer installation begins.

Already familiar with Smarter Access Control? Great! You can take the Fast Track training assessment to complete the training requirement. All training can be found at https://academy.alarm.com/page/access-control or in How can permission be granted to create Access Control accounts and order hardware?.

X1100 Door Controller

The X1100 Door Controller provides local decision making, event reporting, and database storage capabilities for the Alarm.com Smarter Access Control platform. Two reader interfaces provide control for two supervised physical barriers.

For UL compliance, the Power Sourcing Equipment must be UL Listed under UL 294.

Reader ports 1 and 2 can accommodate a reader and provide LED and buzzer control. Form-C contact relay outputs may be used to control locking hardware. The relay contacts are rated at 5 A @ 30 VDC (NO) and 3 A @ 30 VDC (NC), dry contact configuration. The four inputs that are provided may be used for monitoring door position switches or request-to-exit devices. Input circuits can be configured as unsupervised or supervised. The X1100 requires 12 to 24 VDC for power.

The SRAM is backed up by a lithium battery when input power is removed. This battery should be replaced annually. If data in the SRAM is determined to be corrupt after power-up, all data, including flash memory, is considered invalid and is erased. All configuration and cardholder data must be re-downloaded.

Jumper setup

Prior to installation, set the battery and termination jumpers.

Important: Set the battery jumper J4 to ON.

If this step is skipped, the local database will be cleared if the board experiences a drop in power.

Important: If the X1100 will be either the beginning or end of the communication bus, set the end of line termination jumpers J5 and J9 to IN. This configuration is the most common.

Leave the jumper set to OUT only if a single communication bus is wired directly to two expansion modules. This is rare and not recommended unless required to minimize wiring.

DIP switches

The four DIP switches determine the operating mode of the X1100 processor. DIP switches are read on power-up except where noted. The DIP switches are set in the normal operating position (OFF) by default. No action is required.

For information about advanced configurations, see What are the DIP switches used for on an X1100 Door Controller?.

X1100 hardware

X1100 hardware.png

Wiring

Connections
Terminal Label Function
TB1-1 VOUT Reader 1 Power
TB1-2 GND Reader 1 Ground
TB1-3 D0 Reader 1 Data 0/DAT
TB1-4 D1 Reader 1 Data 1/CLK
TB1-5 GND Reader 1 Ground
TB1-6 GRN Reader 1 Green LED
TB1-7 RED Reader 1 Red LED
TB1-8 BZR Reader 1 Beeper
TB1-9 N/C No Connection
TB1-10 GND Reader 1 Ground

TB2-1

TB2-2

IN1 Input 1

TB2-3

TB2-4

IN2 Input 2
TB3-1 NO Relay 1 Normally Open Contact
TB3-2 C Relay 1 Common Contact
TB3-3 NC Relay 1 Normally Closed Contact
TB3-4 NO Relay 2 Normally Open Contact
TB3-5 C Relay 2 Common Contact
TB3-6 NC Relay 2 Normally Closed Contact
TB4-1 VOUT Reader 2 Power
TB4-2 GND Reader 2 Ground
TB4-3 D0 Reader 2 Data 0/DAT
TB4-4 D1 Reader 2 Data 1/CLK
TB4-5 GND Reader 2 Ground
TB4-6 GRN Reader 2 Green LED
TB4-7 RED Reader 2 Red LED
TB4-8 BZR Reader 2 Beeper
TB4-9 N/C No Connection
TB4-10 GND Reader 2 Ground

TB5-1

TB5-2

IN3 Input 3

TB5-3

TB5-4

IN4 Input 4
TB6-1 NO Relay 3 Normally Open Contact
TB6-2 C Relay 3 Common Contact
TB6-3 NC Relay 3 Normally Closed Contact
TB6-4 NO Relay 4 Normally Open Contact
TB6-5 C Relay 4 Common Contact
TB6-6 NC Relay 4 Normally Closed Contact

TB7-1

TB7-2

TMP Tamper

TB7-3

TB7-4

AC AC Fail

TB7-5

TB7-6

BT Battery Fail
TB7-7 GND Input Power Ground
TB7-8 VIN Input Power (from local supply)

TB8-1

TB8-2

TB8-3

TR+

TR-

GND

IO Module Port 1

TB8-4

TB8-5

TB8-6

TR+

TR-

GND

IO Module Port 2
24 VDC and 12 VDC power supplies 

Note: The ADC-AC-X1100 can be powered using 12 or 24 VDC (12 VDC is displayed in diagram below). To power the controller using 24 VDC, connect the 24V power supply to the GROUND and 12-14 VDC terminals instead of a 12V power supply.

X1100 Kit Wiring.png

24 VDC and 12 VDC power supplies.png

Status LEDs  

LED Initialization Normal Operation
BATT FAIL ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
AC FAIL ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
TAMPER ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
IN 1 ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
IN 2 ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
IN 3 ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
IN 4 ON then OFF OFF = Inactive, ON = Active, Flash = Fault*
ONLINE ON for ~ 15 s Off-Line / On-Line and battery status
Off-Line = 20% ON, On-Line = 80% ON
Double flash if battery is low
HOST COMM ON for ~ 1 s Host communication activity (Ethernet)
IO INTERNAL ON for ~ 1 s Internal IO module communication activity
IO MODULE PORT 1 ON for ~ 1 s External IO module activity (Port 1)
IO MODULE PORT 2 ON for ~ 1 s External IO module activity (Port 2)
READER 1 ON for ~ 1 s Flashes when data is received, either input
READER 2 ON for ~ 1 s Flashes when data is received, either input
RELAY 1 OFF ON = Energized
RELAY 2 OFF ON = Energized
RELAY 3 OFF ON = Energized
RELAY 4 OFF ON = Energized
ETHERNET OFF Flashing = Ethernet Activity
ETHERNET JACK OFF Green/Left ON = Good link
Yellow/Right ON = 100 Mb/s
Yellow/Right OFF = 10 Mb/s

*Note: If this input is defined, every three seconds the LED is pulsed to its opposite state for 0.1 seconds. Otherwise, the LED is OFF.

Factory reset

The Factory Reset function can be used for the following purposes:

  • Erase all configuration and cardholder database information.
  • Recover from database corruption causing X1100 board to continuously reboot.
  • Erase any previously configured static IP settings.
Factory reset steps
  1. With the X1100 board powered off, set S1 DIP switches to: 1 & 2 “ON”, 3 & 4 “OFF”.
  2. Apply power to the X1100 board. LED 1 will turn on for about 15 seconds while the X1100 boots up.
     
    Important: Do not remove power during the following steps:
     
  3. Watch for LEDs 1 & 2 and 3 & 4 to alternately flash at a 0.5 second rate; LED 1 will be solid for 15 seconds before this occurs.
  4. Within 10 seconds after the above pattern starts, change switches 1 and 2 to “OFF”.
  5. LED 2 will flash, indicating the configuration memory is being erased. Full memory erasure takes up to 60 seconds.
  6. When complete, only LEDs 1 & 4 will flash for 3 seconds.
  7. The X1100 board will reboot 2 seconds after LEDs 1 & 4 stop flashing (no LEDs are on during this time).

Input power

The X1100 requires 12 to 24 VDC power. Connect power with minimum of 18 AWG wire.

  1. Connect the power ground to earth ground in only ONE LOCATION within the system. Multiple earth ground connections may cause ground loop problems and is not advised.
  2. Observe POLARITY on 12 to 24 VDC input (GND (-) and VIN (+)).

Cabinet tamper and UPS fault input wiring

Connect the AC FAIL (AC+/-) and BATT FAIL (BT+/-) inputs to the corresponding contacts provided on the power supply. Connect the TAMPER input to a tamper switch on the enclosure.

Cabinet tamper and UPS fault input wiring.png

Reader and expansion module wiring

Reader ports
  • Each port can be used to wire one Wiegand or OSDP reader.
  • Readers that require different voltage or have high current requirements should be powered separately.
  • Refer to the reader manufacturer specifications for cabling requirements.
X1100 Description
READER POWER Reader Power 12 VDC
GROUND Ground
D0 / DAT / B Wiegand Data 0, Data line, OSDP B
D1 / CLK / A Wiegand Data 1, Clock line, OSDP A
GROUND Ground (not Shield) - Optional
GREEN LED Green LED - If reader only has one LED wire, use the Green LED terminal
RED LED Red LED
BEEPER Beeper
NO CONNECTION Not used
GROUND Ground (not Shield) - Optional
Reader wiring diagrams
Typical Wiegand readerTypical Wiegand reader.png
Typical OSDP readerTypical_Wiegand_reader_OSDP.png
 
Wiring Expansion Modules

Connect up to 31 total X100 expansion modules using 2-wire RS-485 Expansion Module ports 1 and 2. The last expansion module on the bus must have the termination jumper installed. Use 1-twisted pair, shielded cable, 120Ω impedance, 24 AWG, 4,000 ft. (1,219 m) maximum total length.

Note: For ease of install, daisy chain expansion modules together. Wire each expansion module to the next module instead of wiring directly back to the controller.

 

Wiring expansion modules.png Wiring expansion modules 2.png

Relay wiring

Four Form-C contact relays are provided for controlling door lock mechanisms. The relay contacts are rated at 5 A @ 30 VDC (NO), 3 A @ 30 VDC (NC), dry contact configuration. Each relay has a Common pole (C), a Normally Open pole (NO), and a Normally Closed pole (NC).

When momentarily delivering power to unlock the locking hardware (fail secure), the Normally Open and Common poles are used. When momentarily removing power to unlock the locking hardware (fail safe), the Normally Closed and Common poles are used. Check with local building codes for proper egress door installation.

Caution: Door lock mechanisms can generate EMF feedback to the relay circuit that can cause damage and premature failure of the relay. For this reason, it is recommended that a diode be used to protect the relay.

Relay circuit wiring diagrams
Diode selection: MOV selection:
  • Diode current rating: 1x strike current
  • Diode breakdown voltage: 4x strike voltage
  • Clamp voltage: 1.5x VAC RMS
  • Use UL recognized MOV with appropriate ratings
Diode selection.png MOV selection.png

Input wiring

Inputs are used to monitor door position switches or request-to-exit devices. Input circuits can be configured as unsupervised or supervised. When unsupervised, reporting consists of only the open or closed states.

When configured as supervised, the input circuit will report not only open and closed but also open circuit, shorted, grounded,* and foreign voltage.* A supervised input circuit requires two resistors be added to the circuit to facilitate proper reporting. The standard supervised circuit requires 1k Ω 1% resistors, which should be located as close to the sensor as possible.

*Note: Grounded and foreign voltage states are not a requirement of UL 294 and therefore not verified by UL.

22 AWG minimum required for input wiring. 18 AWG recommended if wiring request-to-exit devices in series with locking hardware.

The input circuit wiring configurations shown are supported but may not be typical:

Input wiring.png

Specifications

The interface is for use in low voltage, Class 2 circuits only. The installation of this device must comply with all local fire and electrical codes.

 

Input power 12 to 24 VDC ±10%, 1.9 A max
Inputs Two dedicated reader inputs
Two independent, dedicated ports: 2-wire RS-485
Four programmable inputs
One dedicated input for each of the following:
Tamper, AC Fail, and Battery Fail
Outputs Four relay outputs 5 A (NO) and 3 A (NC) @ 30 VDC
Two-wire LED control
Single-wire buzzer output
Certifications FCC, CE, UL 294 Certified
Dimensions (W x L x H) 6.46” x 5.51” x 1.02” (164 mm x 140 mm x 26 mm)
Temperature 32°F – 158°F (0°C – 70°C) operational
-67°F – 185°F (-55°C – 85°C) storage
Operating humidity 5% - 85% (non-condensing) RH

Warranty

Alarm.com warrants the product is free from defects in material and workmanship under normal use and service with proper maintenance for one year from the date of factory shipment. Alarm.com assumes no responsibility for products damaged by improper handling or installation. This warranty is limited to the repair or replacement of the defective unit.

There are no expressed warranties other than set forth herein. Alarm.com does not make, nor intends, nor does it authorize any agent or representative to make any other warranties, or implied warranties, and expressly excludes and disclaims all implied warranties of merchantability or fitness for a particular purpose. Returns must be accompanied by a Return Material Authorization (RMA) number obtained from customer service, and prepaid postage and insurance.

Notices

Liability

The Interface should only be used to control exits from areas where an alternative method for exit is available. This product is not intended for, nor is rated for operation in life-critical control applications. Alarm.com is not liable under any circumstances for loss or damage caused by or partially caused by the misapplication or malfunction of the product. Alarm.com’s liability does not extend beyond the purchase price of the product.

FCC.png

This device complies with part 15 of the FCC Rules. Operation is subject to the following two conditions:

  1. This device may not cause harmful interference.
  2. This device must accept any interference received, including interference that may cause undesired operation.