Inconsistent Sensor Activity Monitoring for motion sensors on a SEM-DSC PowerSeries
If a SEM-DSC PowerSeries is reporting inconsistent Sensor Activity Monitoring (SAM) for motion sensors (e.g., reports excessively, infrequently, or not at all), verify the following.
Note:
- Motions are in groups 4, 5, or 6. Generally, this will only impact hardwired sensors.
- Motion activity reported does not trigger alarms even if the panel is armed.
How to resolve
- Verify the SEM-DSC PowerSeries is upgraded to firmware 2.72+ and 191c+.
- The SEM-DSC PowerSeries must be on 2.51+ to be able to upgrade to 2.72. For more information about upgrading SEM-DSC PowerSeries, see Can a SEM-DSC PowerSeries be upgraded remotely?.
- If an upgrade was needed, test the motion sensor again after the SEM is on the updated version.
- If an upgrade was not needed, verify the motion sensor is programmed properly and then test the motion sensor again.