DSC PowerSeries Neo - Battery Replacement
Notice: Installation and maintenance servicing for this device should only be performed by qualified personnel.
|
The content on this page has been written by a third party and is not maintained by Alarm.com. Any questions regarding the installation, maintenance, and/or usage instructions in this guide should be directed to the device manufacturer. To access the full installation guide, see DSC PowerSeries Neo Installation Guide - Panel. |
The battery used for a DSC PowerSeries Neo depends on the desired standby time. Use the chart in this article to determine the required battery. Battery capacity deteriorates with age and the number of charge/discharge cycles. Replace every 3-5 years.
Note: For UL installations, a sealed, rechargeable, lead-acid battery or gel type battery is required to meet UL requirements for power standby times.
The DSC PowerSeries Neo panel can be programmed to charge the battery at 400mA or 700mA. For more information, see [982] Battery Settings on page 120 of DSC PowerSeries Neo Installation Guide - Panel.
Battery selection chart
After calculating the battery capacity (B) for each specific installation, use the following table to determine the battery required to support the main panel in standby mode for:
- 4 hours (UL commercial burglary/residential burglary)
- 12 hours (EN50131)
- 24 hours (UL/ULC residential fire, ULC commercial burglary, ULC commercial fire monitoring - no bell load allowed; INCERT [Belgium])
- 36 hours (NFA2P [France])
The battery size is measured in amp-hours (Ah). The current values in the table denote the maximum current draw permitted to achieve the desired standby time with the listed battery types.
| Battery size | 4 hours | 12 hours | 24 hours | 36 hours |
|---|---|---|---|---|
| 4Ah | 700mA | - | - | - |
| 7Ah | 700mA | 500mA | 250mA | - |
| 14Ah (use 2 x 7Ah batteries connected in parallel, UL/ULC installations only) | 700mA | - | 470mA | - |
| 18Ah | - | - | - | 300mA* |
| 26Ah | - | - | - | 500mA* |
*Use 2 x 7Ah batteries connected in parallel, UL/ULC installations only.
To replace the battery in a DSC PowerSeries Neo:
If desired, put the system in test mode with the monitoring station before proceeding. For more information, see Put a system On Test with the monitoring station.
- Disarm the panel.
- Power off the panel.
- Remove AC power from the panel.
- Disconnect the panel from the mounting plate.
- Unplug the battery connector.
- Remove the old battery.
- Power on the panel.
- Install the new battery by connecting the RED battery lead to the positive battery terminal and the BLACK battery lead to the negative battery terminal.
- Reconnect the panel to the mounting plate.
- Restore AC power to the panel.
Note: Verify the panel does not display a Battery Absent trouble condition. If the keypad still displays a low battery message, the new battery may just need time for the panel to recharge it.