Output Control Expansion Module (ADC-AC-MR16OUT) - Installation Guide

Notice: Installation and maintenance servicing for this device should only be performed by qualified personnel.

Note: This article specifically covers the installation of the Output Control Expansion Module (ADC-AC-MR16OUT). For instructions on how to set up a broader access system, see Smarter Access Control - Quick Start Guide.

The ADC-AC-MR16OUT expansion module provides a solution for controlling 16 additional outputs. Two dedicated inputs are provided for cabinet tamper and UPS fault monitoring. Communication to the Mercury Series Door Controller is accomplished using a 2-wire RS-485 interface. The ADC-AC-MR16OUT requires 12-24 VDC for power. See the following figure for component location.

MR16OutOverview.PNG

Requirements

  • A Smarter Access Control Plus service package

Wiring

Connections
TB1-1 Relay 1 NO Relay 1 Normally Open Contact
TB1-2 Relay 1 C Relay 1 Common Contact
TB1-3 Relay 1 NC Relay 1 Normally Closed Contact
TB1-4 Relay 2 NC Relay 2 Normally Closed Contact
TB1-5 Relay 2 C Relay 2 Common Contact
TB1-6 Relay 2 NO Relay 2 Normally Open Contact
TB2-1 Relay 3 NC Relay 3 Normally Closed Contact
TB2-2 Relay 3 C Relay 3 Common Contact
TB2-3 Relay 3 NO Relay 3 Normally Open Contact
TB2-4 Relay 4 NC Relay 4 Normally Closed Contact
TB2-5 Relay 4 C Relay 4 Common Contact
TB2-6 Relay 4 NO Relay 4 Normally Open Contact
TB3-1 Relay 5 NC Relay 5 Normally Closed Contact
TB3-2 Relay 5 C Relay 5 Common Contact
TB3-3 Relay 5 NO Relay 5 Normally Open Contact
TB3-4 Relay 6 NC Relay 6 Normally Closed Contact
TB3-5 Relay 6 C Relay 6 Common Contact
TB3-6 Relay 6 NO Relay 6 Normally Open Contact
TB4-1 Relay 7 NC Relay 7 Normally Closed Contact
TB4-2 Relay 7 C Relay 7 Common Contact
TB4-3 Relay 7 NO Relay 7 Normally Open Contact
TB4-4 Relay 8 NC Relay 8 Normally Closed Contact
TB4-5 Relay 8 C Relay 8 Common Contact
TB4-6 Relay 8 NO Relay 8 Normally Open Contact
TB5-1 Relay 9 NC Relay 9 Normally Closed Contact
TB5-2 Relay 9 C Relay 9 Common Contact
TB5-3 Relay 9 NO Relay 9 Normally Open Contact
TB5-4 Relay 10 NC Relay 10 Normally Closed Contact
TB5-5 Relay 10 C Relay 10 Common Contact
TB5-6 Relay 10 NO Relay 10 Normally Open Contact
TB6-1 Relay 11 NC Relay 11 Normally Closed Contact
TB6-2 Relay 11 C Relay 11 Common Contact
TB6-3 Relay 11 NO Relay 11 Normally Open Contact
TB6-4 Relay 12 NC Relay 12 Normally Closed Contact
TB6-5 Relay 12 C Relay 12 Common Contact
TB6-6 Relay 12 NO Relay 12 Normally Open Contact
TB7-1 Relay 13 NC Relay 13 Normally Closed Contact
TB7-2 Relay 13 C Relay 13 Common Contact
TB7-3 Relay 13 NO Relay 13 Normally Open Contact
TB7-4 Relay 14 NC Relay 14 Normally Closed Contact
TB7-5 Relay 14 C Relay 14 Common Contact
TB7-6 Relay 14 NO Relay 14 Normally Open Contact
TB8-1 Relay 15 NC Relay 15 Normally Closed Contact
TB8-2 Relay 15 C Relay 15 Common Contact
TB8-3 Relay 15 NO Relay 15 Normally Open Contact
TB8-4 Relay 16 NC Relay 16 Normally Closed Contact
TB8-5 Relay 16 C Relay 16 Common Contact
TB8-6 Relay 16 NO Relay 16 Normally Open Contact
TB9-1 Cabinet Tamper CT Cabinet Tamper
TB9-2 Cabinet Tamper GND Cabinet Tamper
TB9-3 Power Fault BA Power Fault
TB9-4 Power Fault GND Power Fault
TB10-1 2-Wire RS485 Bus TR+

SIO Port

TB10-2 2-Wire RS485 Bus TR- SIO Port
TB10-3   Not Used  
TB10-4   Not Used  
TB10-5   GND Ground
TB11-1 Input/Output Power VIN Input Power 12-24 VDC
TB11-2 Input/Output Power VOUT Output Power
TB11-3 Input/Output Power GND Ground

 

Status LEDs

Power-up:

All LEDs OFF.

Initialization:

Once power is applied, initialization of the module begins.

When initialization is completed, LEDs A, B, CT, and BA are briefly sequenced ON then OFF.

Run time:

After a successful initialization, the LEDs have the following meanings:

  • A LED: Heartbeat and On-Line Status:
    • Off-line: 1 second rate, 20% ON Offline status.png 
    • On-line: 1 second rate, 80% ON Online status.png
  • A LED Error Indication: Waiting for application firmware to be downloaded: 0.1 s ON, 0.1 s OFF
  • B LED: Communication Port Status: Indicates communication activity on the communication port
    • CT: Cabinet Tamper
    • BA: Power Fault
    • LED 1 through 16: Illuminates when output relay OUT 1 (K1), OUT 2 (K2) is energized and so on.

The ADC-AC-MR16OUT accepts 12 to 24 VDC for power on TB7. Locate the power source as close to the ADC-AC-MR16OUT as possible. Make power connection with minimum of 18 AWG wires.

Communication Wiring

The ADC-AC-MR16OUT communicates to an Alarm.com Mercury Series Door Controller using a 2-wire RS-485 interface. The ADC-AC-MR16IN allows for multi-drop communication on a bus of up to 4,000 feet (1219 m). Use twisted pair (minimum 24 AWG) with drain wire and shield for communication. If the ADC-AC-MR16IN is the last device on the communication bus, jumper J1 must be installed.

RS-485 Wiring using the ADC-AC-LP1501 Door Controller

MR16Out Wiring.PNG

Note: For ease of install, daisy chain expansion modules together. Wire each expansion module to the next module instead of wiring directly back to the controller.

Line Termination

For ADC-AC-MR16OUT modules at the end of the communication line, install jumper J1.

Note: The EOL jumper should be installed at both ends of the communication line. This typically includes the controller and last expansion module

Relay Wiring

16 Form-C contact relays are provided for controlling door lock mechanisms or other devices. Each relay has a Common pole (C), a Normally Open pole (NO), and a Normally Closed pole (NC). When momentarily delivering power to unlock the locking hardware (fail secure), the Normally Open and Common poles are used. When momentarily removing power to unlock the locking hardware (fail-safe), the Normally Closed and Common poles are used. Check with local building codes for proper egress door installation. 18 AWG minimum recommended for electric locking hardware.

The current ratings for relay K1 are 5 A @ 30 VDC for normally open (NO) contact and 3 A @ 30 VDC for normally closed (NC) contact. The current rating for relay K2 is 1 A @ 30 VDC. Load switching can cause abnormal contact wear and premature contact failure. Switching of inductive loads (strike) also causes EMI (electromagnetic interference), which may interfere with normal operation of other equipment. To minimize premature contact failure and to increase system reliability, a contact protection circuit may be used.

The following circuit is recommended. Locate the protection circuit as close to the load as possible (within 12 inches [30 cm]), as the effectiveness of the circuit will decrease if it is located far away.

Typical DC Door Strike Wiring

MR16OutPower.PNG    
Diode Selection
  • Diode current rating: 1x strike current
  • Diode breakdown voltage: 4x strike voltage
  • For 12 VDC or 24 VDC strike, diode 1N4002 (100 V/1 A) typical

Inputs for Cabinet Tamper/ Power Fault

Input CT and input BA are used for monitoring cabinet tamper and power failure with normally closed contacts. These two inputs are for contact closure monitoring only, and do not use EOL resistor(s). If these inputs are not used, install a short piece of wire at the input to indicate a safe condition.

MR16Out Inputs.PNG
 

Specifications

Important: The Interface is for use in low voltage, class 2 circuits only. The installation of this device must comply with all local fire and electrical codes.
 

Input Power 12 to 24 VDC ± 10%, 1100 mA max
Communication 2-Wire RS-485
Inputs 2 unsupervised, dedicated for cabinet tamper and UPS fault monitoring
Outputs 16 Form-C relay outputs: Normally Open (NO): 5 A @ 30 VDC resistive, Normally closed (NC): 3 A @ 30 VDC resistive
Certifications UL294 Recognized, FCC Part 15 Class A, CE Compliant, RoHS (2011/65/EU & 2015/863), EU REACH (1907/2006), California Proposition 65, NIST Certified Encryption
Dimensions (L x W x H) 8 x 6 x 1" (20.3 x 15.2 x 2.5 cm)
Temperature

32°F – 158°F (0°C – 70°C) operational

-67°F – 185°F (-55°C – 85°C) storage

Operating Humidity 5-95% (non-condensing) RH

Warranty

Mercury Security warrants the product is free from defects in material and workmanship under normal use and service with proper maintenance for one year from the date of factory shipment. Mercury Security assumes no responsibility for products damaged by improper handling or installation. This warranty is limited to the repair or replacement of the defective unit.

There are no expressed warranties other than set forth herein. Mercury Security does not make, nor intends, nor does it authorize any agent or representative to make any other warranties, or implied warranties, and expressly excludes and disclaims all implied warranties of merchantability or fitness for a particular purpose.

Returns must be accompanied by a Return Material Authorization (RMA) number obtained from customer service, and prepaid postage and insurance.

Liability

The Interface should only be used to control exits from areas where an alternative method for exit is available. This product is not intended for, nor is rated for operation in life-critical control applications. Mercury Security is not liable under any circumstances for loss or damage caused by or partially caused by the misapplication or malfunction of the product. Mercury Security's liability does not extend beyond the purchase price of the product.