LifeSafety Power F8P – Lock Wiring Guide

The F8P is an eight-output fuse-protected power distribution module, used with Alarm.com 4-door pre-wired kits (i.e., ADC-AC-LP1502-PSE and ADC-AC-x1100-4PSE). Each output is individually fused and features both power and fault LEDs for easy diagnostics. The F8P accepts voltages up to 28 VDC and is ideal for controlling magnetic locks, electric strikes, and related Access Control hardware.

Specifications

  • Inputs:
    • 12 VDC or 24 VDC nominal (20 A max per bus)
    • Up to two power buses (B1 and B2) supported
  • Outputs:
    • 8 total zones, each selectable for B1 or B2 voltage, and FAI behavior
    • Fused (3 A ATM style) or PTC (Class 2) protection per output
  • Current:
    • F8: 3 A max per output
    • F8P: 2.5 A max per output (Class 2)
  • Indicators:
    • Bi-color LEDs for B1 and B2 bus power
    • LED for FAI status input

System Wiring

1. Power Input Connections

  • B1 Connectors (i.e., J1 and J4):
    • Connect to primary power supply (DC positive, e.g., FPV4 DC out) for voltage bus B1.
  • B2 Connectors (i.e., J3 and J5):
    • Connect to secondary power supply (DC positive, e.g., B100 DC Out) for voltage bus B2 in dual voltage systems. Leave this disconnected in single voltage systems.
  • BR Connectors (i.e., J3 and J6):
    • Connect all BR (DC common) fastons system-wide for proper operation.

2. FlexIO Connectors

  • Use either FlexIO connector for communication of FAI and Fault signals from an FPO supply and passing the FlexIO bus to additional accessory boards if needed.

Output Zone Wiring (Out1–Out8)

To use the F8P:
  1. Connect the lock
    • While the system is powered down, connect +DC to the terminal marked c of the relay that the lock will be connected to.
    • Connect DC Ground of the lock to the terminal marked Minus.
       
      Note: Verify input power matches the voltage rating of connected locks and system design.
       
  2. Selecting the power selection setting per output:
    • Each jumper on the output will govern how the power output operates. For example, a 24 VDC mag lock that needs to be disabled when the FAI is activated should be wired in to an output on the F8P that is set to position 3 in our ADC-AC-LP1502-PSE kits.

Position

Function

1 (Top)

B1 voltage: Constant output

2

B1 voltage: Enables on FAI

3

B1 voltage: Disables on FAI

4

B2 voltage: Constant output

5

B2 voltage: Enables on FAI

6 (Bot.)

B2 voltage: Disables on FAI

None

Output disabled

FAI (Fire Alarm Interface) Operation

 

 