Output Control Expansion Module (ADC-AC-X300) - Installation Guide

Notice: Installation and maintenance servicing for this device should only be performed by qualified personnel.

Note: This article specifically covers the installation of the Output Control Expansion Module (ADC-AC-X300). For instructions on how to set up a broader access system, see HID Aero Series Smarter Access Control - Quick Start Guide.

The ADC-AC-X300 expansion module provides a solution for controlling 12 additional outputs. Three dedicated inputs are provided for Tamper, AC Fail, and Battery Fail. Two inputs are provided and can be configured as unsupervised or supervised using end-of-line resistors. Communication to the X1100 Door Controller is accomplished using a 2-wire RS-485 interface. The ADC-AC-X300 requires 12-24 VDC for power. See the following figure for component location.

X300 Overview.PNG
 

Wiring

Connections
TB1-1 Relay 1 NO Relay 1 Normally Open Contact
TB1-2 Relay 1 C Relay 1 Common Contact
TB1-3 Relay 1 NC Relay 1 Normally Closed Contact
TB1-4 Relay 2 NO Relay 2 Normally Open Contact
TB1-5 Relay 2 C Relay 2 Common Contact
TB1-6 Relay 2 NC Relay 2 Normally Closed Contact
TB1-7 Relay 3 NO Relay 3 Normally Open Contact
TB1-8 Relay 3 C Relay 3 Common Contact
TB1-9 Relay 3 NC Relay 3 Normally Closed Contact
TB2-1 Relay 4 NO Relay 4 Normally Open Contact
TB2-2 Relay 4 C Relay 4 Common Contact
TB2-3 Relay 4 NC Relay 4 Normally Closed Contact
TB2-4 Relay 5 NO Relay 5 Normally Open Contact
TB2-5 Relay 5 C Relay 5 Common Contact
TB2-6 Relay 5 NC Relay 5 Normally Closed Contact
TB2-7 Relay 6 NO Relay 6 Normally Open Contact
TB2-8 Relay 6 C Relay 6 Common Contact
TB2-9 Relay 6 NC Relay 6 Normally Closed Contact
TB3-1 Input 1 IN+ Input 1
TB3-2 Input 1 IN- Input 1
TB4-1 Relay 7 NO Relay 7 Normally Open Contact
TB4-2 Relay 7 C Relay 8 Common Contact
TB4-3 Relay 7 NC Relay 8 Normally 
Closed Contact
TB4-4 Relay 8 NO Relay 8 Normally Open Contact
TB4-5 Relay 8 C Relay 9 Common Contact
TB4-6 Relay 8 NC Relay 9 Normally Closed Contact
TB4-7 Relay 9 NO Relay 9 Normally Open Contact
TB4-8 Relay 9 C Relay 10 Common Contact
TB4-9 Relay 9 NC Relay 10 Normally Closed Contact
TB5-1 Relay 10 NO Relay 10 Normally Open Contact
TB5-2 Relay 10 C Relay 11 Common Contact
TB5-3 Relay 10 NC Relay 11 Normally Closed Contact
TB5-4 Relay 11 NO Relay 11 Normally Open Contact
TB5-5 Relay 11 C Relay 12 Common Contact
TB5-6 Relay 11 NC Relay 12 Normally Closed Contact
TB5-7 Relay 12 NO Relay 12 Normally Open Contact
TB5-8 Relay 12 C Relay 13 Common Contact
TB5-9 Relay 12 NC Relay 13 Normally Closed Contact
TB6-1 Input 2 IN+ Input 2
TB6-2 Input 2 IN- Input 2
TB7-1 TMP TMP+ Tamper
TB7-2 TMP TMP- Tamper
TB7-3 AC AC+ AC Fail
TB7-4 AC AC- AC Fail
TB7-5 BT BT+ Battery Fail
TB7-6 BT BT- Battery Fail
TB7-7 12-24 VDC GND Input Power Ground
TB7-8 12-24 VDC VIN Input Power Ground (from local power)
TB8-1 EXPANSION IN TR+ IO Module Port 1
TB8-2 EXPANSION IN TR- IO Module Port 1
TB8-3 EXPANSION IN GND IO Module Port 1
TB8-4 EXPANSION OUT TR+ IO Module Port 2
TB8-5 EXPANSION OUT TR- IO Module Port 2
TB8-6 EXPANSION OUT GND IO Module Port 2
TB8-7 12-24 VDC GND Input Power Ground (from local power)
TB8-8 12-24 VDC VIN Input Power Ground (from local power)

Status LEDs

LED Label Represents Initialization Normal Operation
A ONLINE ON then OFF

Heartbeat and Online status

Offline = 1 sec rate, 20% ON

Online = Blinks ON/OFF for 0.7s, ON for 0.3s

B COMM ON then OFF Indicates communication activity on expansion module communication port
BAT BATT FAIL ON then OFF

OFF = Inactive
ON = Active
Flash = Fault*

AC AC FAIL ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
TMP TAMPER ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN1 IN 1 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN2 IN 2 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
D22 Relay 1 OFF ON = Energized
D23 Relay 2  OFF ON = Energized
D24 Relay 3 OFF ON = Energized
D25 Relay 4 OFF ON = Energized
D26 Relay 5 OFF ON = Energized
D27 Relay 6 OFF ON = Energized
D28 Relay 7 OFF ON = Energized
D29 Relay 8 OFF ON = Energized
D30 Relay 9 OFF ON = Energized
D31 Relay 10 OFF ON = Energized
D32 Relay 11 OFF ON = Energized
D33 Relay 12 OFF ON = Energized

Communication Wiring

The ADC-AC-X300 communicates to an X1100 Door Controller using a 2-wire RS-485 interface. The ADC-AC-X300 allows for multi-drop communication on a bus of up to 4,000 feet (1,219 m). Use twisted pair (minimum 24 AWG) with drain wire and shield for communication. If the ADC-AC-X300 is the last device on the communication bus, jumper J1 must be set to IN.

RS-485 Wiring using the ADC-AC-X1100 Door Controller

X300 Wiring.PNG

 

Note: For ease of install, daisy chain expansion modules together. Wire each expansion module to the next module instead of wiring directly back to the controller.

Install jumpers according to the selected configuration

  • If there are additional downstream expansion modules, set jumper to OUT
  • If this is the last device on the communication bus, set jumper to IN
     

X300 Jumper.PNG

Relay Wiring

Twelve Form-C contact relays are provided for controlling door lock mechanisms. Each relay has a Common pole (C), a Normally Open pole (NO), and a Normally Closed pole (NC). When momentarily delivering power to unlock the locking hardware (fail secure), the Normally Open and Common poles are used. When momentarily removing power to unlock the locking hardware (failsafe), the Normally Closed and Common poles are used. Check with local building codes for proper egress door installation. 18 AWG minimum recommended for electric locking hardware.

Note: Load switching can cause abnormal contact wear and premature contact failure. Switching of inductive loads (strike) also causes EMI (electromagnetic interference), which may interfere with normal operation of other equipment.

To minimize premature contact failure and to increase system reliability, a contact protection circuit may be used. The following circuit is recommended. Locate the protection circuit as close to the load as possible (within 12 inches [30 cm]), as the effectiveness of the circuit will decrease if it is located further away.

Use sufficiently large gauge wires for the load current to avoid voltage loss.

X300 Power.PNG    

Diode Selection
  • Diode current rating: 1x strike current
  • Diode breakdown voltage: 4x strike voltage
  • For 12 VDC or 24 VDC strike, diode 1N4002 (100 V/1 A) typical

Input Wiring

There are two inputs that can be used to monitor door position, request-to-exit, or alarm contact devices. Input circuits can be configured as Unsupervised (2 states): reporting as open or closed contact, or Supervised (6 states): reporting as open or closed contact, open circuit, shorted circuit, grounded circuit, or foreign voltage.

A supervised input circuit requires adding two resistors with value of 1k ohm, 1% to the circuit to facilitate proper reporting and should be located as close to the sensor as possible.

The input circuit wiring configurations shown are supported but may not be typical.

22 AWG minimum required for input wiring. 18 AWG recommended if wiring request-to-exit devices in series with locking hardware.

X300 Inputs.PNG

Note: Either the top or bottom 12-24 V terminals can be used to power the board.

Specifications

Important: The Interface is for use in low voltage, class 2 circuits only. The installation of this device must comply with all local fire and electrical codes.
 

Input Power 12 to 24 VDC ±10%, 500 mA max input current
Communication 2-Wire RS-485
Inputs 2 unsupervised/supervised programmable inputs, standard EOL: 1k/1kΩ, 1%, ¼ watt One dedicated input for each: Tamper, AC Fail, Batt Fail
Outputs 12 Form-C relay outputs: 2 A @ 30 VDC resistive
Certifications UL 294 and UL1076 recognized CE compliant FCC Class A ICES-003
Dimensions (L x W x H) 6.46 × 5.51 × 1.02" (16.4 x 14.0 x 2.6 cm)
Temperature

32°F to 158°F (0°C to 70°C) (operational)

-67°F to 185°F (-55°C to 85°C) (storage)

Operating Humidity 5% to 85% (non-condensing) RH

Warranty

Alarm.com warrants the product is free from defects in material and workmanship under normal use and service with proper maintenance for one year from the date of factory shipment. Alarm.com assumes no responsibility for products damaged by improper handling or installation. This warranty is limited to the repair or replacement of the defective unit.

There are no expressed warranties other than set forth herein. Alarm.com does not make, nor intends, nor does it authorize any agent or representative to make any other warranties, or implied warranties, and expressly excludes and disclaims all implied warranties of merchantability or fitness for a particular purpose.

Returns must be accompanied by a Return Material Authorization (RMA) number obtained from customer service, and prepaid postage and insurance

Liability

The Interface should only be used to control exits from areas where an alternative method for exit is available. This product is not intended for, nor is rated for operation in life-critical control applications. Alarm.com is not liable under any circumstances for loss or damage caused by or partially caused by the misapplication or malfunction of the product. Alarm com's liability does not extend beyond the purchase price of the product.

FCC.png

This device complies with part 15 of the FCC Rules. Operation is subject to the following two conditions:

  1. This device may not cause harmful interference.
  2. This device must accept any interference received, including interference that may cause undesired operation.

 