Input Monitor Expansion Module (ADC-AC-X200) - Installation Guide

Notice: Installation and maintenance servicing for this device should only be performed by qualified personnel.

Note: This article specifically covers the installation of the Input Monitor Expansion Module (ADC-AC-X200). For instructions on how to set up a broader access system, see HID Aero Series Smarter Access Control - Quick Start Guide.

The ADC-AC-X200 expansion module provides a solution for controlling sixteen additional inputs. Two Form-C relay outputs may be used to control locking hardware or other devices. Three dedicated inputs are provided for Tamper, AC Fail, and Battery Fail. Input circuits can be configured as unsupervised or supervised using end-of-line resistors. Communication to the X1100 Door Controller is accomplished using a 2-wire RS-485 interface. The ADC-AC-X200 requires 12-24 VDC for power. See the following figure for component location.

X200Overview.PNG
 

Wiring

Connections
TB1-1 Input 1 IN+ Input 1
TB1-2 Input 1 IN- Input 1
TB1-3 Input 2 IN+ Input 2
TB1-4 Input 2 IN- Input 2
TB1-5 Input 3 IN+ Input 3
TB1-6 Input 3 IN- Input 3
TB1-7 Input 4 IN+ Input 4
TB1-8 Input 4 IN- Input 4
TB1-9 Input 5 IN+ Input 5
TB1-10 Input 5 IN- Input 5
TB2-1 Input 6 IN+ Input 6
TB2-2 Input 6 IN- Input 6
TB2-3 Input 7 IN+ Input 7
TB2-4 Input 7 IN- Input 7
TB2-5 Input 8 IN+ Input 8
TB2-6 Input 8 IN- Input 8
TB3-1 Not Used    
TB3-2 Relay 1 NO Relay 1 Normally Open Contact
TB3-3 Relay 1 C Relay 1 Common Contact
TB3-4 Relay 1 NC Relay 1 Normally Closed Contact
TB4-1 Input 9 IN+ Input 9
TB4-2 Input 9 IN- Input 9
TB4-3 Input 10 IN+ Input 10
TB4-4 Input 10 IN- Input 10
TB4-5 Input 11 IN+ Input 11
TB4-6 Input 11 IN- Input 11
TB4-7 Input 12 IN+ Input 12
TB4-8 Input 12 IN- Input 12
TB4-9 Input 13 IN+ Input 13
TB4-10 Input 13 IN- Input 13
TB5-1 Input 14 IN+ Input 14
TB5-2 Input 14 IN- Input 14
TB5-3 Input 15 IN+ Input 15
TB5-4 Input 15 IN- Input 15
TB5-5 Input 16 IN+ Input 16
TB5-6 Input 16 IN- Input 16
TB6-1 Not Used  

 

TB6-2 Relay 2 NO Relay 2 Normally Open Contact
TB6-3 Relay 2 C Relay 2 Common Contact
TB6-4 Relay 2 NC Relay 2 Normally Closed Contact
TB7-1 TMP TMP+ Tamper
TB7-2 TMP TMP- Tamper
TB7-3 AC AC+ AC Fail
TB7-4 AC AC- AC Fail
TB7-5 BT BT+ Battery Fail
TB7-6 BT BT- Battery Fail
TB7-7 12-24 VDC GND Input Power Ground
TB7-8 12-24 VDC VIN Input Power Ground (from local power)
TB8-1 EXPANSION IN TR+ IO Module Port 1
TB8-2 EXPANSION IN TR- IO Module Port 1
TB8-3 EXPANSION IN GND IO Module Port 1
TB8-4 EXPANSION OUT TR+ IO Module Port 2
TB8-5 EXPANSION OUT TR- IO Module Port 2
TB8-6 EXPANSION OUT GND IO Module Port 2
TB8-7 12-24 VDC GND Input Power Ground
TB8-8 12-24 VDC VIN Input Power Ground (from local power)

 

Status LEDs

LED Label Represents Initialization Normal Operation
A ONLINE ON then OFF Heartbeat and Online status Offline = 1 sec rate, 20% ON Online = Blinks ON/OFF for 0.7s, ON for 0.3s
B COMM ON then OFF Indicates communication activity on expansion module communication port
BAT BATT FAIL ON then OFF

OFF = Inactive
ON = Active
Flash = Fault*

AC AC FAIL ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
TMP TAMPER ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN1 IN 1 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN2 IN 2 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN3 IN 3 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN4 IN 4 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN5 IN 5 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN6 IN 6 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN7 IN 7 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN8 IN 8 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN9 IN 9 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN10 IN 10 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN11 IN 11 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN12 IN 12 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN13 IN 13 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN14 IN 14 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN15 IN 15 ON then OFF OFF = Inactive
ON = Active
Flash = Fault*
IN16 IN 16 ON then OFF OFF = Inactive
ON = Active
​​​​​​​Flash = Fault*
D22 RELAY 1 OFF ON = Energized
D33 RELAY 2 OFF ON = Energized

Communication Wiring

The ADC-AC-X200 communicates to an X1100 Door Controller using a 2-wire RS-485 interface. The ADC-AC-X200 allows for multi-drop communication on a bus of up to 4,000 feet (1,219 m). Use twisted pair (minimum 24 AWG) with drain wire and shield for communication. If the ADC-AC-X200 is the last device on the communication bus, jumper J1 must be set to IN.

Note: Both Port 1 and Port 2 terminals for the Expansion Module ports are the same port and are internally connected.

RS-485 Wiring using the ADC-AC-X1100 Door Controller


X200 Wiring.PNG  

Note: For ease of install, daisy chain expansion modules together. Wire each expansion module to the next module instead of wiring directly back to the controller.

Install jumpers according to the selected configuration

  • If there are additional downstream expansion modules, set jumper to OUT
  • If this is the last device on the communication bus, set jumper to IN

X200 Jumper.PNG​​​​​​​

Relay Wiring

Two Form-C contact relays are provided for controlling door lock mechanisms. Each relay has a Common pole (C), a Normally Open pole (NO), and a Normally Closed pole (NC). When momentarily delivering power to unlock the locking hardware (fail secure), the Normally Open and Common poles are used. When momentarily removing power to unlock the locking hardware (failsafe), the Normally Closed and Common poles are used. Check with local building codes for proper egress door installation. 18 AWG minimum recommended for electric locking hardware.

Note: Load switching can cause abnormal contact wear and premature contact failure. Switching of inductive loads (strike) also causes EMI (electromagnetic interference), which may interfere with normal operation of other equipment.

To minimize premature contact failure and to increase system reliability, a contact protection circuit may be used. The following circuit is recommended. Locate the protection circuit as close to the load as possible (within 12 inches [30 cm]), as the effectiveness of the circuit will decrease if it is located further away.

Use sufficiently large gauge wires for the load current to avoid voltage loss.

Typical DC Door Strike Wiring

X200 Power.PNG    
Diode Selection
  • Diode current rating: 1x strike current
  • Diode breakdown voltage: 4x strike voltage
  • For 12 VDC or 24 VDC strike, diode 1N4002 (100 V/1 A) typical

Input Wiring

There are sixteen inputs that can be used to monitor door position, request-to-exit, or alarm contact devices. Input circuits can be configured as Unsupervised (2 states): reporting as open or closed contact, or Supervised (6 states): reporting as open or closed contact, open circuit, shorted circuit, grounded circuit, or foreign voltage.

A supervised input circuit requires adding two resistors with value of 1k ohm, 1% to the circuit to facilitate proper reporting and should be located as close to the sensor as possible.

The input circuit wiring configurations shown are supported but may not be typical.

22 AWG minimum required for input wiring. 18 AWG recommended if wiring request-to-exit devices in series with locking hardware

X200 Inputs.PNG

Note: Either the top or bottom 12-24 V terminals can be used to power the board.

Specifications

Important: The Interface is for use in low voltage, class 2 circuits only. The installation of this device must comply with all local fire and electrical codes.
 

Input Power 12 to 24 VDC ±10%, 300 mA max input current
Communication 2-Wire RS-485
Inputs 16 unsupervised/supervised programmable inputs, standard EOL: 1k/1kΩ, 1%, ¼ watt One dedicated input for each: Tamper, AC Fail, Batt Fail
Outputs Two Form-C relay outputs: 2 A @ 30 VDC resistive
Certifications UL 294 and UL1076 recognized CE compliant FCC Class A ICES-003
Dimensions (L x W x H) 6.46 × 5.51 × 1.02" (16.4 x 14.0 x 2.6 cm)
Temperature

32°F to 158°F (0°C to 70°C) (operational)

-67°F to 185°F (-55°C to 85°C) (storage)

Operating Humidity 5% to 85% (non-condensing) RH

Warranty

Alarm.com warrants the product is free from defects in material and workmanship under normal use and service with proper maintenance for one year from the date of factory shipment. Alarm.com assumes no responsibility for products damaged by improper handling or installation. This warranty is limited to the repair or replacement of the defective unit.

There are no expressed warranties other than set forth herein. Alarm.com does not make, nor intends, nor does it authorize any agent or representative to make any other warranties, or implied warranties, and expressly excludes and disclaims all implied warranties of merchantability or fitness for a particular purpose.

Returns must be accompanied by a Return Material Authorization (RMA) number obtained from customer service, and prepaid postage and insurance.

Liability

The Interface should only be used to control exits from areas where an alternative method for exit is available. This product is not intended for, nor is rated for operation in life-critical control applications. Alarm.com is not liable under any circumstances for loss or damage caused by or partially caused by the misapplication or malfunction of the product. Alarm com's liability does not extend beyond the purchase price of the product.

FCC.png

This device complies with part 15 of the FCC Rules. Operation is subject to the following two conditions:

  1. This device may not cause harmful interference
  2. This device must accept any interference received, including interference that may cause undesired operation.

 